Welcome to kingsnake.com's message board system. Here you may share and discuss information with others about your favorite reptile and amphibian related topics such as care and feeding, caging requirements, permits and licenses, and more. Launched in 1997, the kingsnake.com message board system is one of the oldest and largest systems on the internet.

Click here for Dragon Serpents
https://www.crepnw.com/
Click for 65% off Shipping with Reptiles 2 You

Mark G., thanks for answers, and another Ranco question.....

chrish Dec 07, 2003 10:48 AM

Mark,

Thanks for answering my Ranco question below. It really helped. Now I have a couple more.....

Coil energized (below setpoint) - C connects to NO
Coil de-energized (at or above setpoint) - C connects to NC

So, for running my heat tape, I should have it wired to the NO contact, so that when the temp falls below the setpoint (- the differential), the NO contact will be closed and my tape will come on. Correct?

I actually had wired it the other way (to NC) and to make it work correctly, I had to set it to cool to make it turn the tape on when the temp reached a critical minimum. Now I understand why. Thanks.

Some power relays (relays for carrying a good amount of current) may have one contact heavier-rated than the other. A contact that stays closed can carry alot more current than one which is opened often, because there is an arc on an opening contact if the load is a motor (like an AC unit.) The Ranco may have a higher rated NO or NC contact for that reason, whichever one is used in Cool mode for an AC. I forgot which one you said it was.

So if I have it wired to the NO contact (which is rated at 16 full loaded amps and 15 resistive amps), I can safely use this unit for up to 1800 watts (15x120) of non-motorized heating equipment?

TIA for clearing this up for me.
-----
Chris Harrison

...he was beginning to realize he was the creature of a god that appreciated the discomfort of his worshippers - W. Somerset Maugham

Replies (2)

markg Dec 07, 2003 08:28 PM

You're welcome, Chris. Yes, connect to the NO contact with the unit in heat mode. Then your heat tapes will have power until they reach the high temp cutoff.

Using the NO contact in this manner will allow you up to 16 amps of juice at 110 VAC, or around 1750 Watts of heater power.

chrish Dec 08, 2003 12:05 AM

>>You're welcome, Chris. Yes, connect to the NO contact with the unit in heat mode. Then your heat tapes will have power until they reach the high temp cutoff.
>>
>>Using the NO contact in this manner will allow you up to 16 amps of juice at 110 VAC, or around 1750 Watts of heater power.
-----
Chris Harrison

...he was beginning to realize he was the creature of a god that appreciated the discomfort of his worshippers - W. Somerset Maugham